### 1. CliniMix 2000 TMV Service

Galvin CliniMix 2000 Lead Safe 3/4" thermostatic mixing valve, 201\.70\.02\.00, on its integrated inlet fittings: hot supply at the red\-handled fitting, cold at the blue, mixed outlet below\. Tap any part to see its name\.

A 3D companion to the Installation Instructions \(Revision 2, 20 August 2026\)\. It does not replace them\.

### 2. Specifications \(Figure 1\) · Temperatures

Factory Set Outlet Temperature: 43 \+/\- 2°C · Outlet Temperature Range: 35 \- 50°C¹ · Hot Supply Temperature: 55 \- 90°C · Cold Supply Temperature: 5 \- 30°C · Hot to Mix Temp Differential: Min 10°C · Cold to Mix Temp Differential: Min 5°C

¹ AS4032\.1 \- 2005: approved adjustment range 38 \- 50°C

### 3. Specifications \(Figure 1\) · Pressure and Flow

Static Supply Pressure: Max 1600kPa · Dynamic Inlet Pressure: 20 \- 600kPa · Recommended Supply Pressure Variation \(Hot:Cold or Cold:Hot\): ±10%² · Supply Pressure Loss Ratio: Max 10:1 · Flow Rate to Ensure Stable Operation: Min 4L/min

² For optimal performance it is recommended that the hot and cold water supply pressures be balanced to within ±10%\. Excessive variation in supply pressures may cause changes in outlet temperature\. Notwithstanding the above, compliance with AS3500 must be maintained\.

### 4. Temperature Adjustment · 1

1\. Using a small flat bladed screwdriver, pry the protective cover off the valves \(Figure 4\)\.

Tap the cover to begin\.

### 5. Temperature Adjustment · 2–3

2\. Fit the supplied key over the adjusting spindle \(Figure 4\)\. • To increase the mixed outlet temperature, rotate the spindle anti\-clockwise\. • To decrease the mixed outlet temperature, rotate the spindle clockwise\. 3\. Allow the mixed outlet temperature to stabilize for 60 seconds and once again take a temperature reading\. Repeat the procedure until the desired temperature has been reached\.

### 6. Temperature Adjustment · 4–7

4\. Push the top cover firmly on to the top of the valve until it snaps back into place\. 5\. Check that the outlet temperature is stable over the full range of flow rates and that the flow rate is adequate for the application\. 6\. Close the outlet\. 7\. The mixing valve is now set and locked\.

### 7. Shut Down Test · Cold

Now that the mixing valve has been set and locked it is necessary to perform a shutdown check\. Allow the mixed water temperature to stabilise and note the outlet temperature\. While holding a digital thermometer in the outlet flow, quickly isolate the cold water supply to the valve\. The outlet should quickly cease to flow\. As a rule of thumb the volume should be less than 0\.2L following the isolation\. Restore the cold water supply and after the mixed water temperature has stabilised, record the outlet temperature and ensure it has remained within specification\.

Tap the cold inlet ball valve to isolate the cold supply\.

### 8. Shut Down Test · Hot

Repeat the above test, except this time quickly isolate the hot water supply to the valve\. The outlet flow should quickly slow to a trickle\. As a rule of thumb the trickle should typically be less than 0\.4L following the isolation\. Restore the hot water supply and after the mixed water temperature has stabilised, record the outlet temperature and ensure it has remained within specification\.

Tap the hot inlet ball valve to isolate the hot supply\.

### 9. Mandatory 5 Year Service · 1–2

At intervals not exceeding 5 years, the piston O\-Ring and thermostatic element/piston assembly must be replaced and lubricated\. Lubricant must be potable water approved silicon\-based grease \(supplied with the spare parts kit\)\. Procedure: 1\. Isolate the hot and cold supplies by closing the inlet ball valves\. Vent the outlet pipework at the closest fixture to drain\. 2\. Pry off the plastic cover using a small flat bladed screwdriver or similar\.

### 10. Mandatory 5 Year Service · 3

3\. Remove the brass cap assembly with a suitable spanner\.

Tap the brass cap assembly to begin\.

### 11. Mandatory 5 Year Service · 4–5

4\. Remove the element/piston assembly\. 5\. Remove the piston O\-Ring\. Care must be taken to ensure the internal surfaces of the valve body are not damaged\.

### 12. Mandatory 5 Year Service · Parts \(Figure 6\)

6\. Dispose of plastic cover, brass cap assembly, element/piston assembly and piston O\-Ring\.

Figure 6 callouts: 5\-YEAR SERVICE KIT 201\.79\.10\.09 · Element and Piston Assembly 201\.90\.08\.90 · O\-Ring Kit 201\.90\.01\.90\. Tap a part to see its name and code\.

### 13. Mandatory 5 Year Service · 7–8

7\. Replace both O\-Rings with the parts provided in the spare parts kit \(both O\-Rings are the same size\)\. Ensure the new O\-Rings are clean and lightly greased with the lubricant provided\. 8\. Insert the new element/piston assembly taking great care not to damage the external surfaces of the piston\.

### 14. Mandatory 5 Year Service · 8

8\. … Refit the cap assembly to the body and tighten to a maximum torque of 10Nm\.

### 15. Figure 5 \- Servicing the Inlet Fittings

Strainer cleanliness: 1\. Isolate the hot and cold supplies to the mixing valve by closing the inlet ball valves\. 2\. Remove the inlet fitting strainer cap with a suitable spanner and then remove the mesh strainer, as shown in Figure 5 below\. 3\. The strainers should be cleaned with a dilute water solution of suitable descaling solvent \(such as CLR\), checked for physical damage and then thoroughly rinsed with clean water\. 4\. The strainers can then be re\-installed into the valve, and the top cover replaced and tightened to a maximum torque of 15Nm into the inlet valve bodies\.

Five\-year service, 9\. Clean the isolator strainers … If needed, the 5 Year kit contains new strainers\. Tap the hot strainer cap to begin\.

### 16. Mandatory 5 Year Service · 10

10\. Fully recommission the valve\. Fit the provided plastic cover\.

Commissioning of the Valve is on p\.3 of the Installation Instructions\.

### 17. Fault Finding · 1 of 11

Fault / Symptom: The desired mixed water temperature cannot be obtained or the valve is difficult to set\. Cause: • Hot and cold supplies are fitted to the wrong connections • Valve contains debris • Strainers contain debris • Non\-return devices are damaged Rectification: • Refit the valve with Hot/Cold supplies fitted to the correct connections • Clean valve ensuring debris is removed and components are not damaged • Clean strainers ensuring debris is removed • Check non\-return devices are not jammed\. Clean if necessary

### 18. Fault Finding · 2 of 11

Fault / Symptom: The valve will not shut down\. Cause: • The hot to mix temperature differential is not high enough • Sealing seat is damaged or fouled by debris Rectification: • Raise hot water temperature • Replace piston o\-ring • Clean seat using suitable descaling solution

### 19. Fault Finding · 3 of 11

Fault / Symptom: Mix temperature is unstable\. Cause: • Debris is fouling valve • Flow rate below 4L/min • Strainers are fouled • Systems may be fluctuating outside valve parameters Rectification: • Clean the valve ensuring that all debris is removed and components are not damaged • Rectify any pressure deterioration • Clean strainers • Check system pressure, install pressure control valves to ensure inlet conditions are within specification

### 20. Fault Finding · 4 of 11

Fault / Symptom: Mix temperature changing over time\. Cause: • Inlet conditions \(pressures or temperatures\) are fluctuating • Strainers contain debris Rectification: • Install suitable pressure control valves to ensure inlet conditions are within specification • Clean strainers ensuring debris is removed

### 21. Fault Finding · 5 of 11

Fault / Symptom: Either full hot or cold flowing from outlet fixture\. Cause: • Valve is incorrectly set • Hot/Cold water has migrated to other inlet Rectification: • Adjust mix temperature between 35 \- 50ºC as required • Replace faulty non\-return valves

### 22. Fault Finding · 6 of 11

Fault / Symptom: No flow from the valve outlet\. Cause: • Hot or cold water failure • Strainers are fouled Rectification: • Valve functioning correctly\. Restore inlet supplies and check mix temperature • Clean strainers

### 23. Fault Finding · 7 of 11

Fault / Symptom: Flow rate reduced or fluctuating\. Cause: • Valve or inlet fittings fouled by debris • Dynamic inlet pressures are not within recommended limits Rectification: • Check valve and inlet fittings for blockages • Ensure the dynamic inlet pressures are nominally balanced to within \+/\- 10%

### 24. Fault Finding · 8 of 11

Fault / Symptom: Mixed water temperature too hot or cold\. Cause: • Valve has been tampered with • Valve incorrectly set • Inlet temperatures are not within specified limits Rectification: • Readjust valve to required set temperature • Ensure inlet temperatures are within required limits

### 25. Fault Finding · 9 of 11

Fault / Symptom: Hot water flows into the cold water system or vice versa\. Cause: • Non\-return valves faulty Rectification: • Replace non\-return valves

### 26. Fault Finding · 10 of 11

Fault / Symptom: Valve is noisy\. Cause: • Water velocity above velocity requirements of AS3500 Rectification: • Reduce water velocity

### 27. Fault Finding · 11 of 11

Fault / Symptom: Temperature adjuster difficult to move\. Cause: • Adjustment at maximum mix temperature stops\. • Valve piston over set\. Rectification: • Mixed water is at maximum temperature no higher mix\. • Wind adjuster out until set temperature required is achieved\.

### 28. Where to Find the Service Kit

CliniMix® Lead Safe™ TMV 5\-Year Upgrade/Service Kit 201\.79\.10\.09\. What's Included in the Kit: Red Protective Cover / Top Cap Assembly / Element and Piston Assembly / Mixing Tube / O\-Ring \(Body O\-Ring\) / Temperature Adjustment Key / Allen Key / Grease

Tap an item on the tray to see its name\. Galvin Engineering service\-kit page: galvinengineering\.com\.au/clinimix\-lead\-safe\-tmv\-5\-year\-upgrade\-service\-kit